Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Welded Shear Studs & Composite Floor Deck 1

Status
Not open for further replies.

WWTEng

Structural
Nov 2, 2011
391
Would anybody mind sharing the general structural notes for these two items here! Our library doesn't have these notes so I want a jump start on creating a new set of notes for both.

Thanks in advance.
 
Replies continue below

Recommended for you

I'll see one more time if anyone can share these notes. If not, that's still OK.

Merry Xmas all.
 
Although notes will vary from engineer to engineer, the notes should generally cover the following:

1) diameter and length of headed studs required
2) general instructions of how to layout the studs in the low flutes of the deck
3) Maximum stud spacing along beam, minimum side to side spacing, clearance from edge of beam flange, additional studs, etc.
4) Fastening of deck to beams
5) Removal of ceramic ferrules
6) Restrictions on erection of masonry walls on composite slabs until proper curing.

I hope this helps....
 
Sorry I missed this... from my General Notes:

HEADED STUDS

HEADED STUD MATERIAL TO ASTM A307 AND CSA W59, INCLUDING APPENDICES. MIN GRADE 60 KSI AND WELDABLE

HEADED STUD LENGTH IS TO U/S OF STUD HEAD

MAX HEADED STUD DIA SHALL NOT EXCEED 2-1/2 TIMES BASE MATERIAL THICKNESS

MIN STUD LENGTH TO DIA RATIO FOR HEADED STUDS SHALL BE 4

HEADED STUD SHALL PROJECT 2X STUD DIA INTO CONC OVER STEEL DECK

HEADED STUD LONGITUDINAL SPACING SHALL BE 6X STUD DIA MIN AND TRANSVERSE SPACING SHALL BE 4X STUD DIA MIN

WELD AND TEST HEADED STUDS TO CSA W59, INCLUDING APPENDICES

WELD HEADED STUDS TO STEEL SECTIONS AT LOCATIONS SPECIFIED

DECK FOR WELDING THROUGH SHALL BE 2 SHEETS MAX IN CLOSE CONTACT. THICKNESS OF EACH SHEET SHALL BE [0.060" |1.52MM] (CNT) PLUS Z275 HDG COATING

DO NOT APPLY COATING SYSTEM TO SURFACES TO RECEIVE HEADED STUDS

COMPOSITE CONSTRUCTION IS [SHORED | UNSHORED]

Modify as needed CSA W59 is a Canadian welding code...

Dik
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor