Wet Steam Accumulator Level Control

Status
Not open for further replies.

RJB32482

Chemical
Jan 19, 2005
271
We are looking to install. A wet steam accumulator on our boiler system. We are struggling on level control. I read that the steam entering the vessel refills the vessel water that is flashed off. But someone we visited had a water pipe going into the accumulator from the deaerator. Do we need to control level as the accumulator level is dropping with boiler feedwater or is it just for startup? I read in Spirax Sparco engineering tutorial that just the incoming steam raises the water level. Thanks.
 
Replies continue below

Recommended for you

You need a water level system and feed water pump/s just as you have on the boiler.
Genblr
 
If the energy of the steam (press/temp) entering the accumulator is significantly higher than the accumulator pressure (steam leaving), then you'll tend to lose water. Think of it as an energy balance. If the energy of the entering steam per pound is higher, you won't need the same mass as that leaving to maintain pressure.

If the energy of the steam entering the accumulator is the same as or close to the steam leaving, you'll tend to gain water. This is assuming you're controlling the accumulator pressure.

The reason you're gaining water in the second scenario is that the steam mass entering is the same as what's leaving but you have thermal energy losses through the insulation that energy lost has to be made up for by additional steam (energy) just to maintain pressure.

The change in water level that I've seen (in both scenarios) is slow. The first was addressed by a small manual makeup line from the feed pump discharge. The second was handled by just blowdown. If the plant you visited was operating in the second scenario (gaining water) the line back to the deaerator might have been so they could reclaim the water. A line just from the deaerator to the accumulator doesn't seem like it would be useful in the first scenario (except for startup but even then I'd think it should be from pump discharge).

 