Attached is technical data sheet for a Cutler Hammer HKD3400F 300 Amp circuit breaker.
Per our coordination study we are going to set the breaker at an Instantaneous pickup of 5.
In looking at this sheet and the actual breaker and I'm assuming that means set the one on the far left to 5.
What do the other adjustments do? They aren't in our software to manipulate the TCC curve.