oengineer
- Apr 25, 2011
- 732
What does ACI 350-06 consider to be "Environmental Exposure Conditions" for shrinkage and temperature reinforcement for Mat Foundations?
Section 7.12.2.1 states the following:
"For members subjected to Environmental Exposure Conditions or required to be liquid tight, the area of shrinkage and temperature reinforcement shall provide at least the ratios of reinforcement area to gross concrete area shown in Table 7.12.2.1:
Concrete sections that are at least 24 in. may have the minimum shrinkage and temperature reinforcement based on a 12 in. concrete layer at each face. The reinforcement in the bottom of base slabs in contact with soil may be reduced to 50 percent of that required in Table 7.12.2.1."
The image below is Table 7.12.2.1
Would rain water meet this criteria? This is for a mat foundation being design for an irrigation pump station. The mat foundation is just a solid square block with a filter equipment sitting on top, so liquid tight situation would not apply. The filter equipment & mat foundation will NOT be covered and exposed to rain (whenever it rains).
Suggestions/comments are appreciated.