What Intermediary Relay Should be Used?

Status
Not open for further replies.

jeffl012

Electrical
Jun 19, 2019
8
We have an AccuEnergy EV390 energy meter. We're trying to determine what is the most suitable "Intermediary Relay" (see page 19 for specs) to use in order to latch a Packard C440A 24v coil, 3 phase contactor. The meter has a nice built-in auxiliary power supply that can be used to drive the intermediary relay (see page 14-15 for specs). Can anyone help recommend a good relay for this use case?
Any help is much appreciated!
 
Replies continue below

Recommended for you

I don't see a power supply output on page 14-15. That is the internal power supply for the relay.
It appears that the meter has a relay output capable of 250vac/30vdc and 5A. I don't think you would need an intermediary relay to drive that contractor, but the link doesn't show the coil ratings so I couldn't say for sure.
If you really need a intermediary relay, you could go with something like a KRPA relay. Don't forget to buy the socket also.
 
Sorry, you're correct. Wrong reference. According to the spec sheet, the power supply operating range that could be used to drive the relay is: 100~240Vac, 50/60Hz; 100~300Vdc.
 
Thanks for your help JG2828!
FYI, according to the manufacturer, internal relay has no coil inside (it's a dry switch). They also insist to use an intermediary relay. They said the switch you recommended was fine, but it should be a 5A break current vs 10A.
 