What is positive to negative sequence coupling and negative to positive sequence coupling ?

EddyWirbelstrom

Electrical
Feb 17, 2002
215
When calculating voltage imbalance, what is the positive to negative sequence coupling ( Z12 ) and negative to positive sequence coupling ( Z21 ) at the point of common coupling, in relation to unbalanced voltage ? How is it determined ?
The utility has only provided positive ( Z1 ) , negative ( Z2 ) and zero ( Zo ) sequence impedance at the point of common coupling.
If both Utility ( source ) and load were balanced, there would only be positive sequence currents and voltages.
 
Replies continue below

Recommended for you

See:
EPRI AC Transmission Line Reference Book—200 kV and Above, Third Edition
Chapter 2: Electrical Characteristics of Conductor Configurations and Circuits
 