HI everyone,
I am studying how to place capacitors in a 12kv distribution network and i have a couple of questions that i can't seem to answer with the literature i read.
Lets consider a simple example,suppose you place a fixed capacitor on a 12KV line that is compensating 3 loads. see attachemnt.
now if you want to determine the voltage rise that the capacitor causes , the literature says :
Voltage rise = Capacitor current * system reactance
Where sytem reactance is the reactance between the voltage source and the capacitor.
What i don't understand is : When one or 2 of the loads are put out of service. How does the load that is still in service expercience a higher voltage rise? Because the system reactance didn't change! and the capacitor current didn't not change also. How am i seeing this wrong?
The reason for his question is that the utility has placed a fixed capacitor in an area with residential loads, but when the network was reconfigured, where some load behind the capacitor where shed, some customers claimed to have experienced high voltages.As a result the banks where put out of service.
I want to find out an explanation dor this.
Thanks in advance
I am studying how to place capacitors in a 12kv distribution network and i have a couple of questions that i can't seem to answer with the literature i read.
Lets consider a simple example,suppose you place a fixed capacitor on a 12KV line that is compensating 3 loads. see attachemnt.
now if you want to determine the voltage rise that the capacitor causes , the literature says :
Voltage rise = Capacitor current * system reactance
Where sytem reactance is the reactance between the voltage source and the capacitor.
What i don't understand is : When one or 2 of the loads are put out of service. How does the load that is still in service expercience a higher voltage rise? Because the system reactance didn't change! and the capacitor current didn't not change also. How am i seeing this wrong?
The reason for his question is that the utility has placed a fixed capacitor in an area with residential loads, but when the network was reconfigured, where some load behind the capacitor where shed, some customers claimed to have experienced high voltages.As a result the banks where put out of service.
I want to find out an explanation dor this.