I've got a project where I have some fairly long spanning joists over a gym. Some joists are supported by a stiffened plate seat that the joists sit on.
The joist manufacturer made his joist seat the exact same plan size as my stiffened plate joist seat. Since his seat is the same plan size as my stiffened plate seat, the erector went around the edges of the plate seat/joist seat and welded the edge where the two plates meet.
It looks as though he may have gotten at least a partial penetration weld in there....its does not appear to be just a surface fillet weld....but I"m not sure what this weld should even be considered, and, what the capacity of such a "line weld" would even be.
There is a testing service on site.
I am thinking of having the testing service review the weld and get feed back as to throat thickness of the weld and penetration depth of weld, then, if deep enough, possibly accepting the weld.....or, rejecting it, depending upon the returned data.
The uplift loads are small and the lateral shear load is small.
The joist seat angles are 1/2" thick and the stiffened plate seat is 3/4" thick.
Could this be considered a slot weld?.....and if so, would need to have a 1/2" throat thickness per AISC?
The joist manufacturer made his joist seat the exact same plan size as my stiffened plate joist seat. Since his seat is the same plan size as my stiffened plate seat, the erector went around the edges of the plate seat/joist seat and welded the edge where the two plates meet.
It looks as though he may have gotten at least a partial penetration weld in there....its does not appear to be just a surface fillet weld....but I"m not sure what this weld should even be considered, and, what the capacity of such a "line weld" would even be.
There is a testing service on site.
I am thinking of having the testing service review the weld and get feed back as to throat thickness of the weld and penetration depth of weld, then, if deep enough, possibly accepting the weld.....or, rejecting it, depending upon the returned data.
The uplift loads are small and the lateral shear load is small.
The joist seat angles are 1/2" thick and the stiffened plate seat is 3/4" thick.
Could this be considered a slot weld?.....and if so, would need to have a 1/2" throat thickness per AISC?