Dumbo2929
Electrical
- May 31, 2005
- 109
So my client wants to back-feed a 1000kVA transformer (13.8kV-480V) from the 480V side, to re-power a piece of equipment (connected off the 13.8kV side), and has asked what size circuit breaker would be needed to not trip on inrush. That transformer is about 1200A full load at 480V, and the ANSI inrush point is approx. 10-12X at 0.1 sec. I figure a 1000-1200A circuit breaker (with 10X instantaneous) would work, or a fuse of about 800A would clear the inrush point. Note that the load being fed is very small (<50kW) for a temporary installation. Anyone have any thoughts on these breaker sizes?