sailoday28

Mechanical
Jul 19, 2004
968
What is a realistic temperature to use for CCD? I will be using the hours in conjunction with SEER to estimate future cost for KW-HR for a heat pump. Also how many years back should be included, ie 2012,2011 ,etc?

Thanks
 
Replies continue below

Recommended for you

Get yourself a TMY (typical meteorological year) weather file for your location, free from US DOE at: The TMY is a good statistical average, and it's the standard for energy analysis work.

Here's a discussion that's pretty accurate:
There are lots of conversion programs to turn that TMY file into readable data. This one from the U of Wisconsin Solar Energy Labs puts the TMY directly into Excel:


As for your base temperature, the typical one we pick is 65°F for residential low-rise buildings, 50°-55°F for commercial and institutional spaces (except health care occupancies). Degree days is pretty meaningless for hospitals or any other facility that is heavily internally loaded.



Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
I don't see how cooling degreeday and SEER will help.
First, for cooling you also would need wetbulb degree days and solar radiation. Second, your building, internal loads etc. play a role.
a 8760-hour energy simulation is a must to even have a chance, and event hat is based on many assumptions.
 
Sorry, I will use CDD for summer kw-hrs.
CDD*24 = hours.
DesignTons*hours /SEER =kw-hr
Regards
 
Use TMY and an hourly building occupancy and use schedule.

Degree days are just too course to return anything meaninful.
 