The truss shown below sets on top of a 2”x4”x8’ wall with studs 16” OC; so the bottom chord is around 15’ off the ground and the truss supports are 8’ off the ground. The truss shown is one of a series of trusses set on 24” centers. The bearing wall is freestanding for 14’. Thus there are 7 trusses exerting deflection or lateral force on the freestanding wall. At the ends of the freestanding wall are lateral wall set at 90 degrees which form part of the room. The calculated lateral loads are beyond the capacity of dual 2x4 cap plate and deflections seem excessive. Shown below are 3 examples using a different combination of support connections and the resulting deflection and lateral loads.

QUESTIONS:
1. What combination of support connections should be considered for a freestanding wall?
2. How can the high lateral loads or excessive deflections be addressed?

Table1_x14aka.png

Truss1_isdias.png



Table2_vxma2u.png

Truss2_kvglkt.png



Table3_jyzoly.png

Truss3_e6uyni.png



Note: I substituted a 6”x15# wide flange as a cap plate and a lateral loading of 340# on 24” centers exceeded the capacity of a 6”x15# wide flange. Max Unity Check = [highlight #FCE94F]3.6[/highlight].

Table4_dyccze.png

WF_Loads_haaozv.png

Plan View
WF_Deflection_tvommw.png

Plan View
 
Replies continue below

Recommended for you

Are you planning to add members 26-39 & 32-34 as well as 27-38 & 31-35?

The structure is almost hinged at nodes 23, 26, 32 and 51. If it were completely hinged at those four nodes, the structure would be unstable. Even with the additional members mentioned above, you may want to consider the advisability of approaching so close to an unstable structure.

Have you checked vertical deflection at node 23 with unbalanced snow load?

BA
 
I guess you need to design for moment continuity at those hinges. A very small change in the slope would help enormously, but that'd mean dealing with the architects ?