miketech59
Electrical
- Sep 24, 2005
- 8
Could anyone please advise me ? Currently we are having problems with a Parsons 1963 generation transformer rated at 59MVA with a conservator . The oil is water cooled .The problem seems to be the load Tap changer which for the last ten years has be only changed of-line .Dissolvee gas analysis found high levels of ethylene in the oil. The unit was inspected and no slack connections found .The oil was then filtered . On its return to service the buchoz alarm was triggered after two days .A DGA was done every day on the unit . The results showed Hydrogen 784 at 89.48 ppm per day ,Methane 126.53ppm per day, ethane50.67 ppm per day,ethylene 262.18 ppm per day, acetylene 2.34 ppm per day. The unit cannot be replaced before 2007. What can be done ?