When is a return air and/or relief air fan needed?

Status
Not open for further replies.

ssn61

Mechanical
Mar 30, 2010
72
I like to know, in general, what dictates the fact that a return and/or relief air fan is needed in an air handling unit.
 
Replies continue below

Recommended for you

Static is a primary driver. Put excessively simply, if your return ductwork requires an 1" (250 Pa) of pressure, your space will be pressurized by that amount, unless you provide a return/relief fan.
 
When pressure relationships are important have a supply and return fan with some sort of tracking. In an office or home application with a packaged unit (Carrier, Trane, York, etc.), a relief or exhaust fan can come on during economizer operation to prevent over-pressurization.
 