Soloten
Electrical
- May 29, 2018
- 14
Is an Induction motor considered to be operating at Service Factor 1.0 if it is operating at rated kW output but at 90% rated voltage with 111% of the rated full-load current?
In page 2 in the second paragraph from the link, the author discusses this, but I am not clear as to what the author says with respect to the SF, especially when he mentions, 'If you have a SF of 1.15 for instance, but are operating at rated load, a voltage lower than rated load will not have much negative impact on the performance'. Is he referring to 'rated load' as rate kW output or rated Full load amps?
In page 2 in the second paragraph from the link, the author discusses this, but I am not clear as to what the author says with respect to the SF, especially when he mentions, 'If you have a SF of 1.15 for instance, but are operating at rated load, a voltage lower than rated load will not have much negative impact on the performance'. Is he referring to 'rated load' as rate kW output or rated Full load amps?