I know what a fire flow test is and it has always been my understanding this test should be performed at the very beginning of any project design.
This said I am not asking for help in performing the fire flow calculations because if I am asked I will flat out refuse. How would someone size the mains and place hydrants if they didn't perform the fire flow calculations? If the water wasn't there before I ever got involved with the project how the heck am I supposed to fix it now?
Project consists of a set of four three story residential buildings with the bottom floor, open on all four sides, used for parking cars (OH1) while the second and third floors where residential units. Four units per building.
Civil drawings, prepared by a professional engineer, detail underground mains, sizes, run-in and fire hydrant locations were prepared in early January as were the architectural drawings.
I was invited to bid the job at the end of January and applied for a flow test from the local fire department. My contract begins at a connection 1'-0" AFF of each building.
I asked for a flow test in late April and because of COVID I didn't receive results until the very end of May. The results were:
Static: 55 psi
Residual: 25 psi
Flow: 632 gpm
Certainly not great but as far as sprinklers, and sprinklers only, go it's adequate.
For sprinklers I got everything to work with a minimum 8.4 psi safety factor and that was the OH2 area with 250 gpm hose. My sprinklers worked just fine so I submitted the drawings.
Well, it appears my fire sprinkler drawings have not yet been approved because the project lacks fire flow calculations.
From fire department feedback I am getting the feeling they are looking at me to do the fire flow calculations which is something I have never been asked to do and, in my strong opinion, should have been done by someone else well before the project got started.
How could anyone lay out the site utility drawings without having performed the fire flow calculations? I would have to think a the fire flow calculations would be the very first thing done on any project well before the fire fire sprinkler contractor showed up to bid the project.
I got the feeling I am going to be blamed for the project not having the required fire flow. It appears I have enough for the residential units alone but I am worried about the parking area under the building that is OH1.
Reason there is such a difference in BOR and source pressures is the use of a RPZ backflow assembly.
Oh, and I wouldn't stake my life on it but I think the fire flow for the OH1 area is 1,500 gpm? If I am right someone has a real problem on their hands seeing as how the site utilities have already been installed.
Sorry for the ramble but it is upsetting that someone might be looking at me as if it were my responsibility.
This said I am not asking for help in performing the fire flow calculations because if I am asked I will flat out refuse. How would someone size the mains and place hydrants if they didn't perform the fire flow calculations? If the water wasn't there before I ever got involved with the project how the heck am I supposed to fix it now?
Project consists of a set of four three story residential buildings with the bottom floor, open on all four sides, used for parking cars (OH1) while the second and third floors where residential units. Four units per building.
Civil drawings, prepared by a professional engineer, detail underground mains, sizes, run-in and fire hydrant locations were prepared in early January as were the architectural drawings.
I was invited to bid the job at the end of January and applied for a flow test from the local fire department. My contract begins at a connection 1'-0" AFF of each building.
I asked for a flow test in late April and because of COVID I didn't receive results until the very end of May. The results were:
Static: 55 psi
Residual: 25 psi
Flow: 632 gpm
Certainly not great but as far as sprinklers, and sprinklers only, go it's adequate.
For sprinklers I got everything to work with a minimum 8.4 psi safety factor and that was the OH2 area with 250 gpm hose. My sprinklers worked just fine so I submitted the drawings.
Well, it appears my fire sprinkler drawings have not yet been approved because the project lacks fire flow calculations.
From fire department feedback I am getting the feeling they are looking at me to do the fire flow calculations which is something I have never been asked to do and, in my strong opinion, should have been done by someone else well before the project got started.
How could anyone lay out the site utility drawings without having performed the fire flow calculations? I would have to think a the fire flow calculations would be the very first thing done on any project well before the fire fire sprinkler contractor showed up to bid the project.
I got the feeling I am going to be blamed for the project not having the required fire flow. It appears I have enough for the residential units alone but I am worried about the parking area under the building that is OH1.
Reason there is such a difference in BOR and source pressures is the use of a RPZ backflow assembly.
Oh, and I wouldn't stake my life on it but I think the fire flow for the OH1 area is 1,500 gpm? If I am right someone has a real problem on their hands seeing as how the site utilities have already been installed.
Sorry for the ramble but it is upsetting that someone might be looking at me as if it were my responsibility.