Hi All,
Currently, I'm working at HVAC system which delivered 3°C of chilled water to the HVAC system with 8-9°C return (5-6°C/11°F delta temperature).
The HVAC spec manual specifies that chilled water supply should be at 6°C/43°F and return at 11°C/53°F (5°C/11°F delta temperature)
though the delta temperature is at standard value, engineers here want to raise the chilled water supply temperature in order to save energy. maybe it sounds plausible but wouldn't be any difference if the delta temperature remain the same?
and what's the effect to have such low operating temperature of chilled water?