Why do the standards mention that the pipe length for pressure test should be no longer than 500m.

Status
Not open for further replies.

S06

Mechanical
Jun 15, 2019
9
The standards mentions that the pipes pressure tested should be no longer than 500m.
However, I have installed pvc sewer mainforce line more than 800 meter without conducting pressure test.
I just wanted to know, technical what will happen if we conduct pressure test for pipe length exceeding 500m.
 
Replies continue below

Recommended for you

Well, there's more surface area and volume for elastic expansion of the pipe, so if there's a limit for pressure and/or volume change, you could be more likely to exceed it.
 
Which "standards"??

500m seems a short arbitrary number.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
I witnessed a pressure test of a high pressure gas transmission line that was 2 1/2 miles long. Again, which "Standards"?
 
LittleInch

You are right.

However, our project specification has mentioned:

e. Test sections: Limit test sections in pressure lines to not more than 500 m.

(img ]

I thought this is specified in some standards. However after going through ASTM F 2164 and AWWA i was unable to find any upper limit for pressure test pipe length i.e. "< 500 m".

May be it is only our project specification and not standard.

Thanks for pointing out the point.
 
The only practical limits I would consider is a small leakage rate on a large diameter pipe won't show much pressure loss with longer lengths having more volume. For small diameter pipe would frictional head loss play any role in equalizing.
 