Hi,

I have just obtained some fault currents result from using SKM, it shows that both the SLG and LL(phase to phase) is much higher than the 3ph fault.

With SLG fault I can figure out that it is possible (due to low sequence impedance) but why is the phase to phase fault bigger than the 3ph fault?

Thanks
 
Replies continue below

Recommended for you

Correction...

it should be LLG (double phase to ground fault) not LL....

Why is LLG bigger than 3ph fault? Because of low zero sequence impedance from generators and transformers?

Thanks
 
Delta/wye transformers ahead of the fault location short circuit the upstream zero impedance network regardless of fault type. Any fault involving the zero sequence network will see a low zero sequence value.
 