I'm examining an A36 W12x26 that appears to have failed by web yielding. A W6x15 column, 10' long bears directly on flange of the W12. Web of the column and web of the W12 are in the same plane. The column did not buckle. Since the W12 had a pair of 1/4" x 3" full depth stiffeners at the column location, web crippling appears not to be an issue. Assuming "N" equals 6", I came up with 86 kips as the critical concentrated load for the beam web. However I have reason to believe that the load at failure was much higher. Assuming the stiffeners act as an "extra" web, with "N" equal to 6" and "k" equal to zero, come up with another 54 kips of capacity. Brings the total capacity to 140 kips at failure which seems to fit the conditions. All dimensions and calcs by AISC 9th Edition, ASD. Anyone see flaws in my logic (or arithmetic) or know a better way to analyse this situation? Thanks.