I need to determine if an existing CIP slab section is adequate. I have a segment of a slab that is 8' wide x 12" thick, spanning 25'. There are uniformly spaced longitudinal bars in the bottom (#5 @ 12")along with 2-#11 along each side of this strip. There are #5 @ 12" bottom transverse reinforcement as well.
Is there a limit to the width to depth of a strip in a slab that I can consider as a beam? I know the transverse reinf. is adequate to distribute loads to the additional #11 edge bars,but I don't see a code limit that applies to this condition (considering this strip as a wide beam works for my loading condition).
I also have a similar condtion with a 14' wide strip that also calcs as working except fo deflection.
Thanks for the input!
I need to determine if an existing CIP slab section is adequate. I have a segment of a slab that is 8' wide x 12" thick, spanning 25'. There are uniformly spaced longitudinal bars in the bottom (#5 @ 12")along with 2-#11 along each side of this strip. There are #5 @ 12" bottom transverse reinforcement as well.
Is there a limit to the width to depth of a strip in a slab that I can consider as a beam? I know the transverse reinf. is adequate to distribute loads to the additional #11 edge bars,but I don't see a code limit that applies to this condition (considering this strip as a wide beam works for my loading condition).