moideen
Mechanical
- May 9, 2006
- 360
4 LPs at 37 meters are designed a sump pump for a new project. I just looked at their submission, and from what I can tell, the system head curve isn't shown. This pump will move water at the design head at a rate of 32 l/s instead of 4 l/s, and both the power input and NPSR will go up. The hydraulic data does not match what was asked for or what was planned. If I'm wrong, please correct me.[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1672298787/tips/wilo_sump_pump_bfypdf.pdf[/url]