- Jan 21, 2016
- 114
Hi there,
I'm working on a project, where I need to reinforce a chainlink perimeter fence. The fence recently failed in high winds (not surprising as the posts are undersized and they were not attached to a footing).
I'm trying to determine how best to analyse this. The fence has a privacy screen that is the fake grass type of stuff. This is necessary from a Building Control perspective.
So this leads to my main question :
1. Due to the privacy screen, do I consider the fence as a solid panel? (doing so is leading to some very large overturning moments, which is causing the foundation size to be kind of ridiculous). If not, what guidance can I follow to conservatively estimate what the wind load should be?
Typically for a chainlink fence, I've seen the footings as mass concrete circular pours (~1' diameter up to 4' deep and the post just cast into the pour).
However, the load on the fence from the wind is approximately 13 kN, which leads to an overturning moment of around 20kNm (depending on footing depth).
The current fence posts are spaced at 20'. I plan on putting an intermediate post in, cutting the tributary width in half, however, this still leads to the 13kN load and 20kNm overturning moment.
Is there another practical way that I can reduce the overturning moment/force, other than adding another mid-post?
See fence condition below :
I'm working on a project, where I need to reinforce a chainlink perimeter fence. The fence recently failed in high winds (not surprising as the posts are undersized and they were not attached to a footing).
I'm trying to determine how best to analyse this. The fence has a privacy screen that is the fake grass type of stuff. This is necessary from a Building Control perspective.
So this leads to my main question :
1. Due to the privacy screen, do I consider the fence as a solid panel? (doing so is leading to some very large overturning moments, which is causing the foundation size to be kind of ridiculous). If not, what guidance can I follow to conservatively estimate what the wind load should be?
Typically for a chainlink fence, I've seen the footings as mass concrete circular pours (~1' diameter up to 4' deep and the post just cast into the pour).
However, the load on the fence from the wind is approximately 13 kN, which leads to an overturning moment of around 20kNm (depending on footing depth).
The current fence posts are spaced at 20'. I plan on putting an intermediate post in, cutting the tributary width in half, however, this still leads to the 13kN load and 20kNm overturning moment.
Is there another practical way that I can reduce the overturning moment/force, other than adding another mid-post?
See fence condition below :