Hi All,
I am currently working on a project to be built in Darwin. It is a skillion roof structure with no walls, 42m wide x 105m length with 6m clear height at the low side. It has 16 portal frames spaced at 7m and a 800WB member size. Following the guidelines listed in Appendix E of 1170.2 I am getting considerably high loads. Approx 4.6kN/m wind load along the portal frame profile. The total loads are way more than compared to a fully enclosed condition. Has anyone here had a similar job? Are there any ways to reduce the loads from exposed steel members that is acceptable?
pu: 2.78kPa
Ki: 1.0
Kar: 1.0
Ksh: 1.0
Cfx: 2.05
Cfig: 32.8 (considering 16 portal frames)
Thanks in advance for the responses!
hrbrt372
I am currently working on a project to be built in Darwin. It is a skillion roof structure with no walls, 42m wide x 105m length with 6m clear height at the low side. It has 16 portal frames spaced at 7m and a 800WB member size. Following the guidelines listed in Appendix E of 1170.2 I am getting considerably high loads. Approx 4.6kN/m wind load along the portal frame profile. The total loads are way more than compared to a fully enclosed condition. Has anyone here had a similar job? Are there any ways to reduce the loads from exposed steel members that is acceptable?