Wind loads for wall along property line 1

Status
Not open for further replies.

xez

Structural
Jan 4, 2012
43
I'm designing an exterior wall with metal panels at the edge of a property line. The wall for the building next to it is taller and is also only 2 ft - 3 ft away. Since there is so little room between the walls, how should the wind loads be accounted for in my wall? It doesn't see the full exterior wind load, but I'm skeptical in calling it an interior wall. Any suggestions for this? Are there references to this in ASCE or IBC?

Also, on a related note, if the wall is indeed designed with a lower load, and the adjacent building is demolished for whatever reason in the future, how does that affect my design? I more than likely won't know what's going on with the adjacent building after everything has been constructed.
 
Replies continue below

Recommended for you

I would design it assuming the adjacent building isn't there.
 
You have to design any structure as if the other structures aren't there, for exactly the reason that you bring up.
If the structures are removed, the wind pressures would increase on your structure.

I believe that there's a passage in ASCE-7 that explicitly calls for this, but I don't have the reference at this time.


CF
 
I agree with the above comments. Can't assume wall not designed by you is going to positively affect your design criteria.

I believe 26sig is referring to 27.1.4 in ASCE 7-10
 
Great. Thanks for all the input!
 