RedlineFP
Mechanical
- Sep 8, 2014
- 8
Hello Forum,
I am designing a Community Recreation Center, Two levels and about 20,000 Sq Ft Area.
There is an area with exposed ceiling structure (21' high) having an vertical opening to the floor above which requires water curtain as per 8.15.4.
In the same area one side big glass wall seeing thru the skating rink. My confusion is that do I have to calculate all 3 together (water curtain , Window sprinklers & ceining level sprinklers - 1500sq ft) ?
I have to size a fire pump based on the highest demand. If I calculate all 3 levels together it comes up with insane flow & pressure requirement and leaves tonnes of safety for rest of my calculations. NFPA doesn't say whether I have to calculate all 3 together but at the same time it doesn't allow the opposite either. My thought process is that I should keep the higher demanding areas from the two combinations calcs, Either Water curtain with 1500 Sq ft calc or window sprinklers with 1500 Sq ft calc. But I am not an engineer so I don't back myself up to make such calls.
Will appreciate any help from the forum.
Thanks & regards,
RedlineFP