There was several columns, 5000 psi concrete, and for some reason large patches were needed. Apparently something happend where patches from perhaps 6 inches to 18 inches in diameter and from only about 3 inches to as much as 6 inches deep were needed in the columns. Columns were max 3 feet wide. This was after most elements of the building were in place including the roof, masonry walls, and even some interior finishing was beginning.
The GC decided to take it upon himself, without consulting the Structural Engineer, to tell some masonry grout people to patch the columns. Then he called my field guys out to test it with the WP. When I got the test report, and found out what was happening, I told him to generate an RFI to have the Structural submit the patching requirements with a testing/quality control requirement. Of course he didnt want to, tried to get me to submit something that said the patches and columns were ok, and I told him to forget it.
I told him that the ASTM specifically says that the test if for hardened concrete only, not grout. But I also told him that we just tested this per his request, and the Structural Engineer makes decisions about what is acceptable, it is not my decision, and to submit it for his review.
I dont usually get involved in structural remedies for this type of thing, and in the past I cored columns after high strength epoxy was injected into columns and the outside patched with this, and the Structural Engineer visually inspected the cores and I believe they might have been compressively tested for strength, with epoxy 'planes' in the core.
I was just curious about this particular problem. I only do geotech but get involved in materials testing from time to time.