Windward Drift on Adjacent Structures ASCE7-10

Status
Not open for further replies.

dsweet1984

Structural
Nov 24, 2014
9
US
Team,

I am a bit confused as to why Section 7.7.2 in ASCE7-10 requires "windward" drift load. I am picturing the snow blowing off of this location into the area between the buildings. Unless there is some kind of wind stoppage force due to higher structure I am not understanding. Would someone set me straight.

Thanks!
Dustin
 
Replies continue below

Recommended for you

You hit it on the last part of your statement. Windward drift occurs when wind blows across a lower roof and causes a snow drift up against a higher area of the building. While there is a 3/4 factor in the calculation this condition may control when the lower roof is substantially longer than the upper roof.
 
Thank you very much for the reply. For others reading I should clarify that 7.7.2 refers to "adjacent structures" so the 2 buildings are not in contact (s<20ft). The windward drift we are discussing is resulting from wind blowing from the lower roof towards the higher structure. The result being a truncated drift at the edge / eave of the lower roof. I did see that in the commentary Figure C7-3 shows a diagram of this situation. They show a parapet, but do not require a parapet in the section.

My thinking is that investigation has shown some sort of wind swirling effect that deposits additional snow in this location. The code provisions make sense. I am just curious to learn more about the background of this requirement.

Thanks!
Dustin
 