dougjl
Electrical
- Sep 14, 2001
- 44
I am relocating a 125 HP DC motor from one plant to another and have a question concerning derating the wiring. The old wiring ran in tray and will be placed in coduit at the new location. If I follow what NEC says that 4-6 current carrying conductors in a raceway must have thier ampacities based on 80% of table 310-16. If I run my Armature wires 2-350 MCM (FLA 205A)in a conduit and then add the 2-#12 (8.4A) field wires, it would seem to me that the code would require me to derate all of the wires forcing me to use 500 MCM to stay in code. This seems a bit unreasonable to me as the #12 are an order of magnitude smaller and would seem to have no effect on the larger conductors. Is there something in the code that I am missing or do I really have to derate if I want to stay in "code"
Thanks,
DOug
Thanks,
DOug