Got a question for you guys.
Whenever we want a PLC ON/OFF status for the motor, we would run cables, provide a NO contacts to the PLC in series with the motor starter coil (see attached VACULOADER SCHEM 2.pdf). Now our engineer wanted to use EATON'S electronic overload relay (C441) and wanted to discard that NO contact. I looked at the C441 manual and it does not say how it sends a signal to the PLC whether the motor is ON or OFF.
On the MCC side, of course you'll know if the motor is running or not as the C441 display is mounted on the MCC panel, displaying the power and current measurements. But how does it send the ON/OFF status signal to our PLC and thus to the HMI?
Whenever we want a PLC ON/OFF status for the motor, we would run cables, provide a NO contacts to the PLC in series with the motor starter coil (see attached VACULOADER SCHEM 2.pdf). Now our engineer wanted to use EATON'S electronic overload relay (C441) and wanted to discard that NO contact. I looked at the C441 manual and it does not say how it sends a signal to the PLC whether the motor is ON or OFF.
On the MCC side, of course you'll know if the motor is running or not as the C441 display is mounted on the MCC panel, displaying the power and current measurements. But how does it send the ON/OFF status signal to our PLC and thus to the HMI?