nogienugz
Electrical
- Oct 6, 2007
- 28
Hi,
Got a question on bringing a multi-core control wiring from the PLC cabinet to MCC with type 2B or 2C control wiring. It says in the definition of NEMA that there is interconnection between control terminal blocks among different buckets in the MCC. Does that mean that neutral/common terminals of the buckets are interconnected (daisy chained) to the neutral/common of the master control terminal block in the horizontal/vertical wireway?
If yes, then, will it be OK to just bring 1 common/neutral (just used 1 core from the multi-core cable ) from my PLC panel (say 1 common from 120 VAC signals) and terminate it to the common of the master TB instead of bringing in 1 common to each of the buckets?
Thanks,
Got a question on bringing a multi-core control wiring from the PLC cabinet to MCC with type 2B or 2C control wiring. It says in the definition of NEMA that there is interconnection between control terminal blocks among different buckets in the MCC. Does that mean that neutral/common terminals of the buckets are interconnected (daisy chained) to the neutral/common of the master control terminal block in the horizontal/vertical wireway?
If yes, then, will it be OK to just bring 1 common/neutral (just used 1 core from the multi-core cable ) from my PLC panel (say 1 common from 120 VAC signals) and terminate it to the common of the master TB instead of bringing in 1 common to each of the buckets?
Thanks,