I'm involved with a wind load analysis of a building built in 1987 and am trying to determine the uplift capacity of the roof support structure. The building has interior and exterior cmu bearing walls and a lightweight concrete deck on vent forms attached to bar joists of various spans at 4 ft. o.c.
The C&C pressures for the joists are 57 to 77.4 psf for zones 2 and 3 respectively and the DL is 37.5 psf (22.5 for 0.6DL).
My question is: without any reference concerning joist uplift loading on the as-builts, may I consider some percentage of the load capacity given in the bar joist standard load tables for uniformly distributed load as a capacity in uplift? The bridging shown on the plans seems to follow the requirments of the Steel Joist Institute Specifications. Also, there is a note on the drawings that states: "Bottom chords of joists shall match top chords."
Any advise would be greatly appreciated.
-Jack
The C&C pressures for the joists are 57 to 77.4 psf for zones 2 and 3 respectively and the DL is 37.5 psf (22.5 for 0.6DL).
My question is: without any reference concerning joist uplift loading on the as-builts, may I consider some percentage of the load capacity given in the bar joist standard load tables for uniformly distributed load as a capacity in uplift? The bridging shown on the plans seems to follow the requirments of the Steel Joist Institute Specifications. Also, there is a note on the drawings that states: "Bottom chords of joists shall match top chords."