Wood Connection Help

Status
Not open for further replies.

TRAK.Structural

Structural
Dec 27, 2023
88
0
0
US
Hi All,

Need help figuring out the best way to connect a wood beam to a wood post. See attached. This is at the corner of a structure where beams spanning opposite directions meet over a column. Currently the beam spanning in and out of the page is shown through bolted to a notched section of the column at the top. The beam spanning left/right on the page is where I am having issues. Both beams are part of knee braced frames so there are some loads to resolve but I don't have any good ideas at the moment of what makes the most sense in terms of general connection scheme here.

Any and all suggestions are appreciated.
 
 https://files.engineering.com/getfile.aspx?folder=756a4d2b-9aac-49c5-9c4f-6b195ea4bd7f&file=Screenshot_2024-01-04_232459.png
Replies continue below

Recommended for you

Custom steel won't be an option on this one.

SE2607 - See below, equal loads and geometry, you still choosing screws over bolts??

Screenshot_2024-01-05_190311_hh6aft.png
Screenshot_2024-01-05_190340_lpg84c.png
 
I am pretty anti-notch in general unless it's for timber piles. For me it seems like 50% of these connections become overnotched because of circular saws. I specify Simpson CC/CCQ column caps for almost all of these scenarios. Since one beam is dropped and one flush I'd find a twist connector to transfer any other loads down from the upper beam to the dropped beam.