I have a manufacture building that spans about 107'x75'. It used to have a steel roof, spanning the 107' (partition wall in the center).. burned down, and they ended up going with Gable wood trusses. The wood trusses are spanning the 75' length, peak at gable height is 18 feet, the wall height is about 16 feet. Total building height is about 34'-0". Truss spacing is at 24" o.c. no ceiling or anything below the bottom chord members to help act as a diaphragm. refer to the Image below.
Also, I understand we still are required to design for seismic, but wind controls here and R=2.
I already designed the connections, bond beams, checked the existing walls and foundations due to the new loadings. designed the diaphragm as well. I had a question about the wall that has the gable end above. There is a hinge point, so what are the best way to brace these. kickers to the roof? or a sub diaphragm at the bottom truss chords? or just typical blocking into 1 to 2 truss bottoms are enough?
Thanks
Also, I understand we still are required to design for seismic, but wind controls here and R=2.
I already designed the connections, bond beams, checked the existing walls and foundations due to the new loadings. designed the diaphragm as well. I had a question about the wall that has the gable end above. There is a hinge point, so what are the best way to brace these. kickers to the roof? or a sub diaphragm at the bottom truss chords? or just typical blocking into 1 to 2 truss bottoms are enough?