I'm learning the Force Transfer Around Openings (FTAO) method for wood shear wall design. I followed along the example in APA Technical Note 555 (attached), and everything made sense until I got to the deflection calculations.
The theory:
According to T555, the deflection of each wall pier is calculated then the overall wall deflection is taken as the average of all pier deflections. The end pier deflecting away from the wall interior is assumed to be full height, with the other pier heights starting at the window sill. They also state an assumption that "the FTAO wall is controlled by the deflection of the full-height piers". Each pier deflection is calculated using the 4 term IBC Equation 23-2.
The implementation:
From what I can tell in the T555 example calculation, the wall pier deflection due to hold down elongation is calculated as follows:
1) Calculate overturning moment in pier based on the panel shear adjacent to the opening and the assumed pier height (either full height or partial height, depending on the loading direction and pier location). For pier 1 v = 481 plf, h = 8 ft and b = 4 ft. So M[sub]OT[/sub] = (v*b)*h = (481)(4)(8) = 15,392 ft-lb.
2) Calculate a tension/hold down force based on the pier's OT moment. T = M[sub]OT[/sub]/b = 15,392/4 = 3,848 lb.
3) Prorate the actual elongation based on the calculated tension relative to the published max tension and elongation values. In the example, the hold down manufacturer's allowable force is 2,145 lb at an elongation of 0.128 inches. So d[sub]a[/sub] = (T/Tmax)*d[sub]max[/sub] = (3,848/2,145)*0.128 = 0.2296 inches.
4) Multiply the prorated elongation by the pier's height-to-width ratio to get the lateral pier deflection. So deflection = 0.2296*(8/4) = 0.459 inches.
The head-scratchers:
- The calculated tension and elongation in pier 1 both exceed the hold down manufacturer's allowable values by a fair margin.
- The hold down tension force was previously calculated as 1,538 lb (ASD) using the overall wall dimensions. The deflection calculation used an LRFD factor, so to compare apples to apples I believe the hold down force would be 1,538/0.7 = 2,197 lbs. Again, this is much smaller than the value of 3,848 considered in the elongation/deflection calc.
- Each wall pier has a deflection component based on hold down elongation, even though hold downs are only provided at the ends of the walls (i.e., not all piers have hold downs).
- How can the overall deflection be "controlled by the full height pier", yet is calculated as an average of both full-height and partial-height piers?
I was wondering if anyone has better insight into this method of calculating wall deflection using the FTAO method. The treatment of the elongation term is fuzzy to me and I haven't been able to find much material on the subject.
The theory:
According to T555, the deflection of each wall pier is calculated then the overall wall deflection is taken as the average of all pier deflections. The end pier deflecting away from the wall interior is assumed to be full height, with the other pier heights starting at the window sill. They also state an assumption that "the FTAO wall is controlled by the deflection of the full-height piers". Each pier deflection is calculated using the 4 term IBC Equation 23-2.
The implementation:
From what I can tell in the T555 example calculation, the wall pier deflection due to hold down elongation is calculated as follows:
1) Calculate overturning moment in pier based on the panel shear adjacent to the opening and the assumed pier height (either full height or partial height, depending on the loading direction and pier location). For pier 1 v = 481 plf, h = 8 ft and b = 4 ft. So M[sub]OT[/sub] = (v*b)*h = (481)(4)(8) = 15,392 ft-lb.
2) Calculate a tension/hold down force based on the pier's OT moment. T = M[sub]OT[/sub]/b = 15,392/4 = 3,848 lb.
3) Prorate the actual elongation based on the calculated tension relative to the published max tension and elongation values. In the example, the hold down manufacturer's allowable force is 2,145 lb at an elongation of 0.128 inches. So d[sub]a[/sub] = (T/Tmax)*d[sub]max[/sub] = (3,848/2,145)*0.128 = 0.2296 inches.
4) Multiply the prorated elongation by the pier's height-to-width ratio to get the lateral pier deflection. So deflection = 0.2296*(8/4) = 0.459 inches.
The head-scratchers:
- The calculated tension and elongation in pier 1 both exceed the hold down manufacturer's allowable values by a fair margin.
- The hold down tension force was previously calculated as 1,538 lb (ASD) using the overall wall dimensions. The deflection calculation used an LRFD factor, so to compare apples to apples I believe the hold down force would be 1,538/0.7 = 2,197 lbs. Again, this is much smaller than the value of 3,848 considered in the elongation/deflection calc.
- Each wall pier has a deflection component based on hold down elongation, even though hold downs are only provided at the ends of the walls (i.e., not all piers have hold downs).
- How can the overall deflection be "controlled by the full height pier", yet is calculated as an average of both full-height and partial-height piers?
I was wondering if anyone has better insight into this method of calculating wall deflection using the FTAO method. The treatment of the elongation term is fuzzy to me and I haven't been able to find much material on the subject.