ivymike
Mechanical
- Nov 9, 2000
- 5,653
hi, I'm wondering whether anyone has experience configuring a woodward 2301 governor to work w/ an electronically governed diesel engine (Caterpillar C280). I've got a C280 recently added in with several 3616s sharing load in a stationary powergen application. Each has its own 2301 governor, and I'm trying to get the gains set correctly for the electronic engine. I've actually never messed with a 2301 governor before, so this is new to me. Planning to use single-point gain maps to get a feel for what settings give startup/no-load stability, with the gain ratio set to 1, then move those settings to the lowest point on a 5pt gain map, populate the rest of the map, and try to to take load. I gather that it's typical to have gain higher at the higher load points, perhaps dropping back a bit at 100% load. I'm not so sure what values of "actuator compensation" and "reset" are appropriate for an electronic engine. Seems to be most stable with very high actuator compensation, but some feedback I got was "if that was a mechanical actuator, it would have broken hours ago- it would be buzzing back and forth." Very low "reset" also seems to help.
Trouble is that I've so far had trouble getting gain high enough to avoid overshoot on startup while still getting stable idle operation... perhaps the gain ratio can help me there? "rpm window" setting of 17rpm currently...
any pointers/experiences would be appreciated.
Trouble is that I've so far had trouble getting gain high enough to avoid overshoot on startup while still getting stable idle operation... perhaps the gain ratio can help me there? "rpm window" setting of 17rpm currently...
any pointers/experiences would be appreciated.