Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Wound Rotor Motors

Status
Not open for further replies.

boomer957

Electrical
Jul 31, 2003
2
Wondering how you can start a WRM W/O the Strating Resistors racked in and not burn up the rotor windings?
 
Replies continue below

Recommended for you

You are correct! Most WRIM do not have the necessary rotor reactance to limit the stator current. You may get lucky but it is NOT a good idea.
 
Doug,

Thanks, I was very sure that this was the case. I pulled the string on this matter and found out that they are opening a valve upstream of this pump/motor and allowing it to free wheel on system pressure prior to starting the motor. This limlits the "locked rotor" inrush current.

While I still believe that this is a very risky practice it seems to be allowing the start of these WRM's.

Wierd huh.

Rob Coffee
Allied Services Group
 
Suggestion: If the motor shaft load torque-speed curve permits, use a suitable soft starting arrangement.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor