Hi all,
I have 2 wound rotor motors each of 22 kW.
We shorted the rotors at the slip ring so that it would behave like a squirrel cage one then used VFD for each.
It worked well. It is now one year since and so far no problems have been recorded.
My question is if i can replace the 22 kW wound rotor motor (shorted) with a 22 kW squirrel cage (with VFD of course)?
Because i've heard that if i want to do, it will require more powered squirrel cage motor (45kW) which will be the equivalent of 22kW wound rotor motor?