if it is a centrifuge, then be guided by the posts of those with direct experience.
The ten minute starting time is new to me.
However, the Star/Delta motors and motor starters that I am familiar with in industrial settings do not have two seperate windings, one Wye and one Delta.
They have three windings. The windings are connected in Wye for starting and reconnected in Delta for running.
To connect in Wye, three leads have to be connected together.
Heating in a winding is dependant on the current in the winding. On the wye connection, the motor current will equal the winding current. On Delta the motor current will be 1.73 times the winding current. In a Star Delta motor both ends of all three windings are brought back to the starter. The
winding current is monitored by an overload device that may be physically located next to the contactor which completes the Star connection.
The question is:
Is the Delta winging shunted, or is the protection shunted while on the Wye connection.
If you have mistaken the contactor that completes the Wye connection for a "Delta Shunting" contactor, then most likely everything is as it should be and the windings are properly protected by the existing overload device.
I'm worried about the 10 minutes starting time. If it is the actual starting protection that is "Shunted" during starting, then disregard this and reread raef's post.
Remember, there is NOT a Wye and a Delta winding. There are three windings that are reconnected in Wye or Delta.