noel0589
Electrical
- Sep 23, 2004
- 50
First off, I'd like to thank all responders, some more than others... you know who you are!!!
I have a problem with my delta contacts (open transition) which seem to be burning out on our hydraulic elevator systems. The only reason I heard that makes sense is because of the surge which can occur during the instant of switching from wye to delta.
Now... the actual physical problem is that roughly 1 in every 4 or 5 starts is when an abnormal amount of arcing/sparking occurs. Does this mean that 1 in every 4 or 5 starts the contactor is closing upon a critical point on the applied voltage wave resulting in a huge surge?
Also, the abnormal amount of sparking always seems to appear on ONLY ONE of the lines, the arcing is not distributed among the three lines. So one contact in the housing has much more deterioration than the others. Is this also a symptom of wye to delta transition current surges?!?! THANK YOU!
I have a problem with my delta contacts (open transition) which seem to be burning out on our hydraulic elevator systems. The only reason I heard that makes sense is because of the surge which can occur during the instant of switching from wye to delta.
Now... the actual physical problem is that roughly 1 in every 4 or 5 starts is when an abnormal amount of arcing/sparking occurs. Does this mean that 1 in every 4 or 5 starts the contactor is closing upon a critical point on the applied voltage wave resulting in a huge surge?
Also, the abnormal amount of sparking always seems to appear on ONLY ONE of the lines, the arcing is not distributed among the three lines. So one contact in the housing has much more deterioration than the others. Is this also a symptom of wye to delta transition current surges?!?! THANK YOU!