Engineer1916
Electrical
- Jan 9, 2020
- 42
Hello,
I have a 25MVA GSU for a solar field YDY configuration. There is no load on Delta, it is only there for stability/Harmonic suppression. I have a couple of questions about the buried delta.
1. Under what conditions should we bring out the corner of a burred delta outside the tank through bushings? What sort of testing is performed on delta winding?
2. How to select the MVA and kV rating of tertiary winding if it is not used for any load?
3. Under what conditions is it better to corner ground this delta winding vs not grounding it?
Thank you in advance.
I have a 25MVA GSU for a solar field YDY configuration. There is no load on Delta, it is only there for stability/Harmonic suppression. I have a couple of questions about the buried delta.
1. Under what conditions should we bring out the corner of a burred delta outside the tank through bushings? What sort of testing is performed on delta winding?
2. How to select the MVA and kV rating of tertiary winding if it is not used for any load?
3. Under what conditions is it better to corner ground this delta winding vs not grounding it?
Thank you in advance.