rockman7892
- Apr 7, 2008
- 1,171
Looking at an application where a new 24.9kV - 12.47kV transformer is being added for interconnection of wind farm to utility 24.9kV distribution line. Transformer is 15MVA and will have delta side facing generation (with grounding transformer on that side) and the wye side facing 24.9kV distribution. The wye point will be bonded to ground with a CT monitoring this connection wtih 51N for rapid detection of site generation feeding into a ground fault on distribution feeder.
The 24.9kV distribution line appears to have a neutral in the form of a multiground neutral on the distribution feeder with the neutral being used for L-N connections of 1-Ph transformers etc... on distribution system.
With the addition of the new interconnection transformer should this neutral be connected directly to neutral HO bushing on wye side of transformer? As I mentioned, this HO bushing will be bonded to local ground but trying to understand how to connect neutral coming into site (neutral is concentric cable neutral coming up with UG risers from main OH line). Should this neutral just be carried to first disconnect means (recloser) ground point?
We will have a 1-Ph station service transformer between incoming and transformer so thinking we need to at least carry the neutral in for that.