kellyo3
Electrical
- Jun 18, 2008
- 4
I am looking for some insight this configuration we are experiencing problems with: I have a distribution transformer that is configured wye-wye, 4160-480/277, 3W, 3P. No neutral is brought out from my switchgear to this transformer, only an equipment ground. The transformer secondary has the X0 connection bonded to the transformer casing, effectively grounded. The load is 3-phase motors with electronic soft-starters. My starters keep shutting down and so far I have not been able to get the alarm code off of the them before the electrician resets them. But in doing so, they start right back up, run for a while then one may shut off again. We are measuring about a 6% voltage drop at the transformer secondary (250-volts) on b-phase only, while a and c phase are slightly above 277 phase to ground. Line to line secondary voltage seems fine. My thought is that the voltages are unstable due to the ungrounded primary neutral, but the motor load on the secondary sees only line-to-line voltage which seems okay. Could these starters be shutting down due to harmonics and interference due to the transformer connections??? If so, any recommendations on how to mitigate? Replacing with a delta-wye transformer is not feasable. Any input would be much appreciated! Thanks