I am using SKM to analyze a system and the utility gave me the values in the following format..
12.47 kV source
Source Impedance
Z1 = 2.602 + j 45.463% 100MVA base ( 0.040 + j 0.707 Ohms)
Z0 = 0.918 + j 39.123% 100MVA base ( 0.014 + j 0.608 Ohms)
Fault Availability
Three-Phase = 10167 A, 219.6 MVA
Phase-Ground = 10668 A
My understanding is that the X/R would be X(Z1)/R(Z1) for the 3 phase fault and (2*X(z1)+X(z0))/(2*R(z1)+R(z0)) for the line to ground faults but the values are not looking correct to me...
Can someone give me a check on this? I'm getting 3 phase X/R of 17.675.