MineGuy
Electrical
- May 29, 2006
- 20
Hi,
I came across a short circuit study done by engineers of
Schd. Electric. It was contracted by our company to them.I read it and came across few things. They assumes 3 Phase X/R ratio of utility to be same as single Phase for X/R ratio. I know three phase ratio is used for calculating the asymmetrical component of contribution but what is the relevance of single phase X/R and how we can assume same as equal.
My other question, Single Phase to ground fault can only be greater than Three phase fault in case if fault occurs on the stator terminals of a solidly grounded generator.
These Sch, Electric guys had also Single line to ground fault current greater than Three phase on MCC bus. I have yet to simulate my self actually in SKM as I use ETAP but I asked this question here to get the concept.
Thanks
I came across a short circuit study done by engineers of
Schd. Electric. It was contracted by our company to them.I read it and came across few things. They assumes 3 Phase X/R ratio of utility to be same as single Phase for X/R ratio. I know three phase ratio is used for calculating the asymmetrical component of contribution but what is the relevance of single phase X/R and how we can assume same as equal.