I'm not an engineer so bear with me on this question.
We have 3 xfmrs in a Substation; 2 are 10,000Kva and 1 is 5000Kva. 13.8 Kv Primary/ 4160 v secondary. They can be tied together via bus tie breakers on the 4160 side. We changed the CT wiring at the 5000kva and used the Line Diff ct's for the Xfmr Diffs and vis a versa. We moved the wires from the terminal block using corresponding numbers,(3C1 to 1C1, 3C2 to 1C2, 3C3 to 1C3, 3C0 to 1C0).
We energized the transformer primary first and as soon as we picked up the secondary main we had an 86 Lockout from the 87T relays(HU). Since we had noticed a wiring problem on the terminal block we tried moving the wires in different combinations(123,312,etc.) until the breaker stayed in.(I know this is not how to do it but the original installation had 4 problems in the xfmr diff scheme and we had no prints or wiring diagrams.)
We showed about 200amps on the secondary which was tied to the bus along with (1) 10,000kva transformer, the other was being repaired for leaks. We kept the 5000Kva on the bus for about 15 minutes with no problem.
Later the other xfmr was energized and leaked more than before, so our boss put the 5000kva on line and had diff lockout with Phase 1&3 targets. Tried again Phase 2 target and lockout.
We are going to check ct wiring tomorrow. Could we have a polarity problem due to the change from a ct in the rrear of the breaker to a ct on the load side stabs of 13,8 kv breaker.
thanks for any suggestions.
Ron
We have 3 xfmrs in a Substation; 2 are 10,000Kva and 1 is 5000Kva. 13.8 Kv Primary/ 4160 v secondary. They can be tied together via bus tie breakers on the 4160 side. We changed the CT wiring at the 5000kva and used the Line Diff ct's for the Xfmr Diffs and vis a versa. We moved the wires from the terminal block using corresponding numbers,(3C1 to 1C1, 3C2 to 1C2, 3C3 to 1C3, 3C0 to 1C0).
We energized the transformer primary first and as soon as we picked up the secondary main we had an 86 Lockout from the 87T relays(HU). Since we had noticed a wiring problem on the terminal block we tried moving the wires in different combinations(123,312,etc.) until the breaker stayed in.(I know this is not how to do it but the original installation had 4 problems in the xfmr diff scheme and we had no prints or wiring diagrams.)
We showed about 200amps on the secondary which was tied to the bus along with (1) 10,000kva transformer, the other was being repaired for leaks. We kept the 5000Kva on the bus for about 15 minutes with no problem.
Later the other xfmr was energized and leaked more than before, so our boss put the 5000kva on line and had diff lockout with Phase 1&3 targets. Tried again Phase 2 target and lockout.
We are going to check ct wiring tomorrow. Could we have a polarity problem due to the change from a ct in the rrear of the breaker to a ct on the load side stabs of 13,8 kv breaker.
thanks for any suggestions.
Ron