jmrockwell
Electrical
- Oct 27, 2006
- 1
I have been told that in a 3 phase Y lighting panel that the nutral must be larger than the phase wires because of the possible imbalance of the loads. The worst unbalance I can think of would be to have one phase to nutral loaded and the other phases with no load!? That would provide the same current in the nutral as the phase. It seemes any other combination would be less in the nutral!? What am I missing?