My client has a system with two 2M DG sets, 12.47kV on a paralleling board. Each is grounded via an 18 ohm resistor. We are proposing to add a third - the gear is set up for eight ultimately. My concern - 18 ohms seems like a rather low resistance value, esp. for what could be eight units in parallel. Should I be concerned for the potential damage if there is a winding ground fault? I'm trying to decide if we should recommend increasing the grounding resistance.
GF protection is 87G and 51N. Windings are 2/3 pitch.
Thanks.