SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
Other than being the first to do an annual inspection the company I work for nor I had anything to do with this recently completed (last few years) project.
A picture is worth a thousand words.
Correct me if I am wrong but the only way this could be "right" would be if an FPE signed off on it using the equivalency clause in NFPA #13 but I find it hard to believe any of you FPE's would do it.
Not that it matters but I couldn't tell if the sidewalls were standard or extended coverage.
I looked for a head in the top of Cupola and didn't see one. The top of the cupola has to be at least 12' to 15' above the sidewall heads.
Per NFPA #25 do I write it up or not? How am I to know an FPE didn't sign off on it?
If I understand it correctly my job in inspecting is to assume everything was correctly installed and approved when it was new and my job is limited to inspecting what is there and what is there will operate.
Am most interested in hearing what you FPE's that do inspections, I know there are a couple, would do with this one.
And there is no fix. A clay tile roof sits on top.... I don't have a clue to a fix other than tearing the roof off or lowering the ceiling.
Thanks much.
A picture is worth a thousand words.
Correct me if I am wrong but the only way this could be "right" would be if an FPE signed off on it using the equivalency clause in NFPA #13 but I find it hard to believe any of you FPE's would do it.
Not that it matters but I couldn't tell if the sidewalls were standard or extended coverage.
I looked for a head in the top of Cupola and didn't see one. The top of the cupola has to be at least 12' to 15' above the sidewall heads.
Per NFPA #25 do I write it up or not? How am I to know an FPE didn't sign off on it?
If I understand it correctly my job in inspecting is to assume everything was correctly installed and approved when it was new and my job is limited to inspecting what is there and what is there will operate.
Am most interested in hearing what you FPE's that do inspections, I know there are a couple, would do with this one.
And there is no fix. A clay tile roof sits on top.... I don't have a clue to a fix other than tearing the roof off or lowering the ceiling.
Thanks much.