From reading the excerpt below from IEC 60076-8, I'm interpreting Z0 to be .85-0.9 the value of Z1. Is this a correct interpretation? I've recently seen utilities/ISOs requesting Z0 data on transformer during the interconnection studies and I can't seem to get a good understanding on this topic.
"The magnetizing impedance Zm which is also indicated in figure 11, is usually neglected in calculations for this winding combination. It is accepted that the zero-sequence impedances of the diagram differ somewhat from values measured with positive sequence current. The difference depends on the arrangement of the windings with respect to each other and usually stays within 10 % to 15 %"
"The magnetizing impedance Zm which is also indicated in figure 11, is usually neglected in calculations for this winding combination. It is accepted that the zero-sequence impedances of the diagram differ somewhat from values measured with positive sequence current. The difference depends on the arrangement of the windings with respect to each other and usually stays within 10 % to 15 %"