Young's/Elastic Modulus of Cement Mortor

Status
Not open for further replies.

Arbu

Structural
Mar 25, 2018
69
Dear All,

I need to model cement Mortar in one software, please suggest me the E value I should assign for that. I Searched a lot but not getting. Please suggest E value for Normal mortar of Proportion in range of 1:3 to 1:4 and normal water content.


Regards,
Sigma
 
Replies continue below

Recommended for you

Your masonry code should have this information. May vary from jurisdiction to jurisdiction.

Dik
 
Yup, check your masonry code. I assume you're modeling an actual member comprised of a unit (concrete block, clay brick etc...) and mortar. in the US ACI code allows 900 f'c and 700 f'c for CMU and clay masonry respectively. I use 1350 ksi for a 1500(f'c)concrete masonry wall (standard) here in the US. It all depends on your materials and may vary greatly.
 
Than you so much Eng. Dik and Eng. Mjkkb2.
 
OP: We're glad to help...

Dik
 